If it were necessary to bond both ends, wouldn't we need a bond bushing every place that reducer washers are used?
I can think of 2 instances where it is not practical to bond both ends. Is it nessesary to bond both ends of the armour?
What about in the case of emt?
If it were necessary to bond both ends, wouldn't we need a bond bushing every place that reducer washers are used?
Generally, the armour of armoured cables "shall be mechanically and electrically continuous throughout" as required in 12-608.
However, where single-conductor AC is installed in such a manner as to prevent the flow of sheath currents, it should be "bonded to ground at the supply end only, and thereafter - - - - isolated from ground." 10-302(2)
Ed
<font size="2" face="Verdana, Helvetica, sans-serif">No. Consider the situation where conduit is adapted to pvc. The end at the pvc adapter isn't separately bonded.What about in the case of emt?