    I can think of 2 instances where it is not practical to bond both ends. Is it nessesary to bond both ends of the armour?

    What about in the case of emt?

  2. #2
    Inactive Member twh's Avatar
    Join Date
    April 3rd, 2002
    Posts
    93
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    If it were necessary to bond both ends, wouldn't we need a bond bushing every place that reducer washers are used?

  3. #3
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Generally, the armour of armoured cables "shall be mechanically and electrically continuous throughout" as required in 12-608.

    However, where single-conductor AC is installed in such a manner as to prevent the flow of sheath currents, it should be "bonded to ground at the supply end only, and thereafter - - - - isolated from ground." 10-302(2)

    Ed

  4. #4
    Inactive Member twh's Avatar
    Join Date
    April 3rd, 2002
    Posts
    93
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    What about in the case of emt?
    <font size="2" face="Verdana, Helvetica, sans-serif">No. Consider the situation where conduit is adapted to pvc. The end at the pvc adapter isn't separately bonded.